    I cannot disable screen blanking with MagicMirrorOS
    27 Posts 3 Posters 10.6k Views 3 Watching
      smegbadger
      @karsten13 unfortunately that change did not prevent the display from dropping. There’s no time timestamp in the docker logs for labwc but when i looked this morning there were some 40 calls to wlr-randr that had failed. If they are every 15mins that’s about 10:00 it failed. I will make a more accurate observation tonight
      karsten13K 1 Reply Last reply
      • karsten13K
        karsten13 @smegbadger
        @smegbadger
        I expected this already …
        can you post the exact error message of wlr-randr when it fails?
        Other point: What happens if you disable MMM-Universal-Pir for a test? Are you still getting the errors or does mm runs correctly over night?
        • karsten13K
          karsten13 @karsten13
          for testing I added wlopm to the current mm-develop docker image.
          So for another test use this lines in the .env file
          MM_IMAGE="karsten13/magicmirror:develop"
          LABWC_IMAGE="karsten13/labwc:develop"
          Then change the on/off commands in the config.js
                                  module: "MMM-Universal-Pir",
                                          onCommand: "wlopm --on HDMI-A-1",
                                          offCommand: "wlopm --off HDMI-A-1",
          and then do a docker compose pull && docker compose up -d
            smegbadger
            @karsten13 I left it running overnight with the MMM-Universal-Pir config lines commented out and the monitor physically switched off and this morning MM was still working fine when I switched the monitor back on again. When I looked at docker logs labwc the wlr-randr command was failing (still being triggered every fifteen mins) which suggests the connection between the MMM-Universal-Pir and the display driver is the issue rather than the display actually going off. I will try your new build today although i will have to add --transform 90 to the onCommand to get my screen rotation.
            magicm@magicmirror:/opt/mm/mounts/config $ docker logs labwc
            HDMI-A-1 "Raspberry PI RPI MON156 81005568472 (HDMI-A-1)"
              Make: Raspberry PI
              Model: RPI MON156
              Serial: 81005568472
              Physical size: 350x190 mm
              Enabled: yes
              Modes:
                1920x1080 px, 60.000000 Hz (preferred, current)
                1920x1080 px, 59.939999 Hz
                1920x1080 px, 50.000000 Hz
                1920x1080 px, 48.000000 Hz
                1920x1080 px, 47.952000 Hz
                1280x720 px, 60.000000 Hz
                1280x720 px, 59.939999 Hz
                1280x720 px, 50.000000 Hz
                1280x720 px, 48.000000 Hz
                1280x720 px, 47.952000 Hz
                720x576 px, 50.000000 Hz
                720x480 px, 60.000000 Hz
                720x480 px, 59.939999 Hz
                640x480 px, 60.000000 Hz
                640x480 px, 59.939999 Hz
              Position: 0,0
              Transform: 90
              Scale: 1.000000
              Adaptive Sync: disabled
            failed to connect to display
            magicm@magicmirror:/opt/mm/mounts/config $ docker exec -it labwc bash
            pi@c7c64f70849e:/$ wlr-randr
            pi@c7c64f70849e:/$
            Steve
              smegbadger
              @karsten13 my apologies, I see the transform is not needed as you have taken the rotation into account
                smegbadger
                @karsten13 the display failed today as before but we have timestamps in the labwc docker logs
                magicm@magicmirror:~ $ docker logs labwc
                00:00:00.000 [INFO] [seatd/seat.c:48] Created VT-bound seat seat0
                00:00:00.000 [INFO] [seatd/seatd.c:194] seatd started
                00:00:00.052 [INFO] [seatd/server.c:145] New client connected (pid: 17, uid: 1000, gid: 1000)
                00:00:00.052 [INFO] [seatd/seat.c:239] Added client 1 to seat0
                00:00:00.052 [INFO] [seatd/seat.c:563] Opened client 1 on seat0
                00:00:00.120 [ERROR] [EGL] command: eglQueryDeviceStringEXT, error: EGL_BAD_PARAMETER (0x300c), message: "eglQueryDeviceStringEXT"
                executing: wlr-randr --output HDMI-A-1 --transform 90
                Sat Mar 29 08:14:25 UTC 2025
                  Make: Raspberry PI
                  Model: RPI MON156
                  Serial: 81005568472
                  Enabled: yes
                  Modes:
                  Position: 0,0
                  Transform: 90
                  Scale: 1.000000
                Sat Mar 29 08:29:25 UTC 2025
                  Make: Raspberry PI
                  Model: RPI MON156
                  Serial: 81005568472
                  Enabled: yes
                  Modes:
                  Position: 0,0
                  Transform: 90
                  Scale: 1.000000
                Sat Mar 29 13:14:26 UTC 2025
                  Make: Raspberry PI
                  Model: RPI MON156
                  Serial: 81005568472
                  Enabled: yes
                  Modes:
                  Position: 0,0
                  Transform: 90
                  Scale: 1.000000
                Sat Mar 29 13:29:26 UTC 2025
                Sat Mar 29 13:44:26 UTC 2025
                Sat Mar 29 13:59:26 UTC 2025
                Sat Mar 29 14:14:26 UTC 2025
                Sat Mar 29 14:29:26 UTC 2025
                Sat Mar 29 14:44:26 UTC 2025
                Sat Mar 29 14:59:26 UTC 2025
                Sat Mar 29 15:14:26 UTC 2025
                Sat Mar 29 15:29:26 UTC 2025
                Sat Mar 29 15:44:26 UTC 2025
                Sat Mar 29 15:59:26 UTC 2025
                Sat Mar 29 16:14:26 UTC 2025
                There's also a new item in the `mm` docker logs when I restarted the docker containers on my return
                Gdk-Message: 16:25:24.348: Error reading events from display: Broken pipe
                [entrypoint 16:25:25.533] [INFO]   ***WARNING*** could write to /etc/localtime
                [entrypoint 16:25:25.539] [INFO]   copy default modules
                [entrypoint 16:25:25.603] [INFO]   copy css files
                Steve
                • karsten13K
                  @smegbadger
                  I build another new labwc image. You can revert the changes done to MM_IMAGE and the on-/offCommand in your setup.
                  The new karsten13/labwc:develop now runs labwc with pid=1 (I thought that was already the case) and additionally kills labwc if the wlr-randr command fails with failed to connect to display.
                  Now the container will restart if labwc is terminated inside the container. This does not address the root issue but should be a good workaround (hopefully).
                  So please do again a docker compose pull && docker compose up -d to get the latest changes …
                    smegbadger
                    @karsten13, thank you for this. It worked well overnight last night. One question: when the wlr-randr command fails, the labwc container is then killed and then automatically restarts - will the screen be turned on then until the next PIR activity and subsequent timeout of MMM-Universal-Pir?
                    Steve
                    • karsten13K
                      @smegbadger said in I cannot disable screen blanking with MagicMirrorOS:
                      yes, I tested this by killing and restarting the labwc-container from outside.
                      Not nice but I have no idea how to solve this.
                        smegbadger
                        @karsten13 I thought that would be the case. I tried changing the initial RANDR_PARAMS="--output HDMI-A-1 --transform 90" in the .env file to RANDR_PARAMS="--output HDMI-A-1 --off" so that the MMM-Universal-Pir module would be responsible for the first switch on of the display but then I got no display on restart at all.
                        Steve
                        karsten13K 2 Replies Last reply
                        • karsten13K
                          @smegbadger
                          had to write it down:
                          labwc	after start			wlr-randr --output HDMI-A-1 --transform 90
                          mm	starts and mm is displayed
                          mm	offCommand			wlr-randr --output HDMI-A-1 --off
                          mm	still up but not displayed
                          labwc	fails after a while, killed
                          mm	still up and displayed again
                          so another idea would be to execute the command defined in RANDR_PARAMS only if the display is not switched off. Will check if I can get this information …
                          • karsten13K
                            @smegbadger
                            I think I have now a working solution for this.
                            For testing
                            use LABWC_IMAGE="karsten13/labwc:develop" in .env.
                            In /opt/mm do
                            # check if worktree is clean
                            git status
                            # switch to develop branch
                            git switch develop
                            # pull
                            git pull
                            Go to /opt/mm/run and execute docker compose pull and docker compose up -d --force-recreate.
                            With these changes the screen should still be blank after a restart of the labwc-container if the screen was blank before. Let me know if it works.
                              smegbadger
                              @karsten13 unfortunately that didn’t work.
                              In the morning the screen was off and could not be restored with docker rm -f labwc && docker compose up -d or docker compose up -d --force-recreate. In both cases the console briefly came back and then the the monitor slept again. Only when i when into the labwc container and did wlr-randr --output HDMI-A-1 --on --transform 90 did the display return. At that point the MMM-Universal-Pir started counting down too and it works as normal.
                              magicm@magicmirror:/opt/mm/run $ docker rm -f labwc && docker compose up -d
                              labwc
                              [+] Running 2/2
                               ✔ Container mm     Running        0.0s
                               ✔ Container labwc  Started        0.5s
                              magicm@magicmirror:/opt/mm/run $ docker compose up -d --force-recreate
                              [+] Running 2/2
                               ✔ Container mm     Started        1.7s
                               ✔ Container labwc  Started        1.8s
                                   >>> still no screen output <<<
                              magicm@magicmirror:/opt/mm/run $ docker exec -it labwc bash
                              pi@3f4fb5c07c91:/$ wlr-randr
                                Make: Raspberry PI
                                Model: RPI MON156
                                Serial: 81005568472
                                Enabled: no
                                Modes:
                                  1920x1080 px, 60.000000 Hz (preferred)
                              pi@3f4fb5c07c91:/$ wlr-randr --output HDMI-A-1 --on --transform 90
                                   >>> screen returns <<<
                              pi@3f4fb5c07c91:/$
                              Please check I did the pull etc correctly
                              magicm@magicmirror:/opt/mm $ git status
                              On branch master
                              Your branch is up to date with 'origin/master'.
                                (use "git add <file>..." to update what will be committed)
                                (use "git restore <file>..." to discard changes in working directory)
                                      modified:   install/install.sh
                              Untracked files:
                                (use "git add <file>..." to include in what will be committed)
                                      install/install.sh.old
                                      run/douglas.env
                              no changes added to commit (use "git add" and/or "git commit -a")
                              magicm@magicmirror:/opt/mm $ git switch develop
                              M       install/install.sh
                              branch 'develop' set up to track 'origin/develop'.
                              Switched to a new branch 'develop'
                              magicm@magicmirror:/opt/mm $ git pull
                              remote: Enumerating objects: 32, done.
                              remote: Counting objects: 100% (32/32), done.
                              remote: Compressing objects: 100% (22/22), done.
                              remote: Total 22 (delta 14), reused 0 (delta 0), pack-reused 0 (from 0)
                              Unpacking objects: 100% (22/22), 2.66 KiB | 247.00 KiB/s, done.
                              From https://gitlab.com/khassel/magicmirror
                                 f4542dd..4891458  develop    -> origin/develop
                                 a4a4748..c4bb59c  master     -> origin/master
                               * [new tag]         v2.31.0    -> v2.31.0
                              Updating f4542dd..4891458
                              Fast-forward
                               .gitlab-ci.yml            |  2 +-
                               build/labwc/Dockerfile    |  2 +-
                               build/labwc/entrypoint.sh | 58 ++++++++++++++++++++++++++++++++++++++++++++++++++--------
                               run/includes/labwc.yaml   |  4 +++-
                               run/original.env          |  4 ++--
                               5 files changed, 57 insertions(+), 13 deletions(-)
                              magicm@magicmirror:/opt/mm $ cd /opt/mm/run
                              magicm@magicmirror:/opt/mm/run $ docker compose pull
                              [+] Pulling 15/15
                               ✔ labwc Pulled        107.9s
                                 ✔ f07a03696dcc Already exists        0.0s
                                 ✔ 98d9f29a8bdf Pull complete        106.0s
                                 ✔ 6c9aae6d02f4 Pull complete        106.1s
                                 ✔ 9d496899b308 Pull complete        106.2s
                               ✔ magicmirror Pulled        171.5s
                                 ✔ d9b636547744 Already exists        0.0s
                                 ✔ 2fb5eed0caf7 Already exists        0.0s
                                 ✔ f51205ec4ac4 Already exists        0.0s
                                 ✔ d7b57be0135b Already exists        0.0s
                                 ✔ 813d7d6819ab Already exists        0.0s
                                 ✔ 9e1af87e1f78 Pull complete        1.1s
                                 ✔ 27001e96a2b0 Pull complete        1.3s
                                 ✔ deb26dbf1268 Pull complete        110.8s
                                 ✔ 1b7abece8518 Pull complete        169.7s
                              [+] Running 2/2
                               ✔ Container labwc  Started        24.9s
                              Steve
                              • karsten13K
                                yes
                                this seems to become a never ending story …
                                With the last changes I wrote the display state (on or off) to a temp file so the labwc container knows the last state even after a restart. Problem now is the mm container, here the logs after restart:
                                > magicmirror@2.32.0-develop start:wayland
                                > WAYLAND_DISPLAY="${WAYLAND_DISPLAY:=wayland-1}" ./node_modules/.bin/electron js/electron.js --enable-features=UseOzonePlatform --ozone-platform=wayland
                                [2025-04-04 21:19:30.050] [LOG]   Starting MagicMirror: v2.32.0-develop
                                [2025-04-04 21:19:30.084] [LOG]   Loading config ...
                                [2025-04-04 21:19:30.087] [LOG]   config template file not exists, no envsubst
                                [2025-04-04 21:19:30.608] [INFO]  Checking config file /opt/magic_mirror/config/config.js ...
                                [2025-04-04 21:19:30.674] [INFO]  Your configuration file doesn't contain syntax errors :)
                                [2025-04-04 21:19:30.675] [INFO]  Checking modules structure configuration ...
                                [2025-04-04 21:19:30.778] [INFO]  Your modules structure configuration doesn't contain errors :)
                                [2025-04-04 21:19:30.780] [LOG]   Loading module helpers ...
                                [2025-04-04 21:19:30.786] [LOG]   Initializing new module helper ...
                                [2025-04-04 21:19:30.788] [LOG]   Module helper loaded: MMM-Universal-Pir
                                [2025-04-04 21:19:30.788] [LOG]   No helper found for module: alert.
                                [2025-04-04 21:19:30.793] [LOG]   Initializing new module helper ...
                                [2025-04-04 21:19:30.793] [LOG]   Module helper loaded: updatenotification
                                [2025-04-04 21:19:30.794] [LOG]   No helper found for module: clock.
                                [2025-04-04 21:19:30.924] [LOG]   Initializing new module helper ...
                                [2025-04-04 21:19:30.925] [LOG]   Module helper loaded: calendar
                                [2025-04-04 21:19:30.926] [LOG]   No helper found for module: compliments.
                                [2025-04-04 21:19:30.927] [LOG]   No helper found for module: weather.
                                [2025-04-04 21:19:31.034] [LOG]   Initializing new module helper ...
                                [2025-04-04 21:19:31.034] [LOG]   Module helper loaded: newsfeed
                                [2025-04-04 21:19:31.035] [LOG]   All module helpers loaded.
                                [2025-04-04 21:19:31.043] [LOG]   Starting server on port 8080 ...
                                [2025-04-04 21:19:31.046] [WARN]  You're using a full whitelist configuration to allow for all IPs
                                [2025-04-04 21:19:31.681] [LOG]   Server started ...
                                [2025-04-04 21:19:31.683] [LOG]   Connecting socket for: MMM-Universal-Pir
                                [2025-04-04 21:19:31.684] [LOG]   Connecting socket for: updatenotification
                                [2025-04-04 21:19:31.685] [LOG]   Starting module helper: updatenotification
                                [2025-04-04 21:19:31.686] [LOG]   Connecting socket for: calendar
                                [2025-04-04 21:19:31.687] [LOG]   Starting node helper for: calendar
                                [2025-04-04 21:19:31.688] [LOG]   Connecting socket for: newsfeed
                                [2025-04-04 21:19:31.689] [LOG]   Starting node helper for: newsfeed
                                [2025-04-04 21:19:31.690] [LOG]   Sockets connected & modules started ...
                                The container is running but electron not (the line Launching application. is missing), I think it is waiting for an active display …
                                The Pir-Sensor which would active the screen again is running inside mm (which is not really running).
                                So I have no idea at the moment, maybe we have to live with the situation before, where after restart we need a sensor interval before the screen is blanked again.
                                  smegbadger
                                  @karsten13 thank you for all the effort you are putting into this issue. I agree, let’s go back to the version that will kill and restart the container if the display doesn’t respond to wlr-randr (and then waits for a MMM-Universal-Pir cycle to sleep it again).
                                  Steve
                                  • karsten13K
                                    Well, it is a pleasure to have such a good tester as you
                                    for now I did exactly this, but this issue is still working in my brain …
                                    So to revert all the changes done before:
                                    cd /opt/mm
                                    git switch master
                                    git pull
                                    Change the images back to latest in .env:
                                    MM_IMAGE="karsten13/magicmirror:latest"
                                    LABWC_IMAGE="karsten13/labwc:latest"
                                    Get new images and restart:
                                    cd /opt/mm/run
                                    docker compose pull
                                    Last point: You should add the --transform 90 to the onCommand of the MMM-Universal-Pir config:
        deactivateDelay: 30000,
        onCommand: "wlr-randr --output HDMI-A-1 --transform 90 --on",
                                    • S smegbadger referenced this topic on